Protection: breakers, fuses and SCCR
Circuit breakers, fuses, short-circuit current ratings and coordination.
Latest articles
How-to
Estimating transformer inrush current for protection coordination
The rules of thumb are screening gates, not coordination inputs: reported inrush runs 8 to 30 times full-load current and lasts 10 cycles to a minute. Plot the decay curve Ipu = 6 × t^-0.31 with t in seconds — it passes through 25× at the first peak, 12× five cycles in and 3× at 10 s — keep the protective device curve above it and below the transformer damage curve, and handle cold-load pickup separately.
Comparison
What current-only motor protection can and cannot detect
Three per-phase current amplitudes support overload, phase loss, current unbalance, stalled acceleration and short-cycling protection, and nothing else. Undervoltage, ground fault, winding temperature and mechanical overloads such as high head pressure need their own inputs: a voltage measurement channel, a core-balance current transformer, and temperature or pressure sensors.
How-to
Closed delta transformer fault current calculation
Compute each delta branch from its own kVA and impedance, then take phasor differences at the line terminals: for a 150 kVA leg with two 100 kVA legs at 240 V and 3.3% Z each, the bolted three-phase terminal fault is highest at each end of the 150 kVA winding and lower at the junction of the two 100 kVA windings. Size secondary equipment on the higher terminal value.