Electrical safety and codes
Electrical safety, arc flash, lockout and the codes and standards behind them.
Latest articles
Explainer
NEC motor branch circuit #14 AWG with a 20 A breaker
#14 AWG is the code-correct conductor for a 3 HP, 230 V three-phase motor with 9.6 A full-load current on a 20 A inverse-time breaker. The 15 A small-conductor cap yields because Article 430 of the NEC specifically permits motor-circuit sizing: 430.22 requires 12.0 A of ampacity, which #14 THHN's 21 A clears, and 430.52 allows the breaker up to 24 A — provided a separate overload relay protects the motor.