Power quality and harmonics
Harmonics, sags, transients and power factor: what they do to equipment and how to find them.
Latest articles
Troubleshooting
Setting voltage imbalance limits on a 480 V phase monitor
Keep voltage unbalance at the motor terminals at 1% or less to run full rated power; above that NEMA MG 1 requires derating, reaching 75% of rated power at 5%, with operation above 5% not recommended. A monitor set to 15% voltage imbalance is far too loose to protect a motor. Measure A-B, B-C and C-A at the starter stopped and running, and at the main panel, and call the utility only when the main panel itself is unbalanced.
Troubleshooting
Diagnosing current imbalance across every motor on a service
Compute unbalance per NEMA MG-1 as maximum deviation from the three-phase average, not the min-to-max spread: a 13% spread is 6.5% unbalance. Identical A-mid, B-low, C-high readings on ten different motors mean the asymmetry is upstream of the machines, so measure voltage unbalance and negative sequence at the motor terminals and current sharing in the parallel feeder sets, not ten motor circuits.
How-to
Where to connect power factor correction on a star-delta starter
Connect a star-delta starter's power factor correction bank on the line side of the contactors, never at the motor terminals of an open transition, with its own Article 460 disconnect, overcurrent protection and conductors at 135 percent of capacitor current. If the bank must sit downstream of the overload relays, route its leads through the sensing elements or resize the relays to the reduced current.
How-to
Assessing VFD harmonics when one small drive runs a plant
No filter is justified on ratings alone: 6 hp × 0.746 kW/hp = 4.48 kW is 6.6% of 68 kW connected capacity. Measure voltage THD at the shared bus with the drive off and then running, and read the drive's input current. If the bus stays under IEEE 519's 5% THD limit with no single harmonic above 3%, leave it alone; if it climbs over, an input reactor on the drive is the fix.