Motors and motor starters
Induction and servo motors, starters, contactors, overloads and motor control centres: selection, sizing and troubleshooting.
Latest articles
Selection guide
Setting overload relays for high-inertia motor starts
Set the current dial at the motor's nameplate full-load current and buy starting time with the trip class, not with a higher setting: Class 10 holds starts up to about 7 s at 600 percent, Class 20 to about 14 s, Class 30 to about 21 s. Longer starts need reduced-current starting, not a bigger relay.
Comparison
Insulation resistance testing from switchgear vs motor terminals
Test from the switchgear with the cable connected for routine trending against a commissioning baseline taken in the same configuration; the cable is a parallel path, so the connected reading sits below the motor alone and moves slowly as the winding degrades. When the trend falls or the decision is about the motor itself, break the circuit and test the motor and cable separately.
How-to
Wiring overload relay contacts to the coil and the PLC
The overload relay's NC trip contact (95-96) belongs in series with the contactor coil so a trip drops the motor out even while the PLC still commands run; the NO auxiliary (97-98) is a separate status input to the PLC. A PLC input is not overload protection, because no general-purpose controller input is a listed motor overload device, so a panel wired the other way needs rewiring.
Explainer
Why motor current rises when voltage exceeds nameplate
A supply 4% above nameplate sits inside the ±10% band NEMA MG1 Part 12 expects motors to tolerate. The power equation gives a lower current only if efficiency and power factor are held fixed; rising magnetizing current near saturation can push measured current back up, so keep the nameplate full-load rating and treat the recalculated figure as an estimate.
Explainer
Running a three-phase motor on single-phase 208 V
Yes — a spinning three-phase motor fed across two terminals regenerates the third leg, but winding heating caps it near 30-40% of rated horsepower, so it is a bench trick, not a supply. For real loads, use a rotary phase converter with an idler at least the next size above the largest motor, or a single-phase-input VFD for motors only — never a drive for amplifiers or power supplies.
Troubleshooting
Why motors burn up with no overload trips on 480 V
Crystallized insulation several feet back from motor terminals is the signature of high-resistance terminations cooking the leads from I²R heat, while unbalanced voltage adds negative-sequence heating that current-magnitude overload heaters never see. Record all three line-to-line voltages and all three phase currents under load, verify the transformer grounding, and measure insulation resistance on every failed branch before any restart. Welded contacts and ruptured starters are consequences of closing onto failed motors, not a separate mystery.
Troubleshooting
Motor starters trip when MCC doors are closed
The trips are real protection, not nuisance: a thermal overload relay without ambient compensation responds to enclosure air temperature, so doors open plus a fan suppresses trips while motor heating continues. A 10-12 V spread on 480 V is 1.0% to 1.7% voltage unbalance, above the NEMA MG 1 limit of 1.0%, and a 60-70 A current spread is severe. Close the doors, pull the fan, and fix the upstream supply that survived the chiller and MCC replacement.
Explainer
Converting a 350 kVA soft start limit to starting current
A 350 kVA soft start limit is about 421 A of line current at 480 V: divide 350,000 VA by √3 × 480 V. The figure is apparent power, so no power factor enters the conversion, and it carries no duration — that comes from the torque-speed margin. The 12.5 kV fuse is a coordination problem; motor protection belongs at 480 V.
Troubleshooting
Why power cables hum during motor startup
The hum is electromagnetic force between the phase conductors, not imbalance: attraction and repulsion reverse every half-cycle, loading the cables at 120 Hz, and force follows current squared. A 538 A start against 84 A running is 6.40 times the current and about 41 times the force. Restrain the conductors and cut the starting current; the measured numbers do not implicate the motor.
Troubleshooting
Troubleshooting intermittent instantaneous motor start trips
An intermittent instantaneous trip on motor start is usually the random closing angle of the contactor, not a failing motor. A first peak can reach about 2.8 times the symmetrical locked-rotor current, so only starts that close near a voltage zero hit magnetic pickup. Capture all three phase currents, rank contactor pole, winding, rotor and breaker causes, and let the trip follow the part you roll.
How-to
Motor starting voltage dip calculation on an 11 kV bus
A starting medium-voltage motor dips the bus in proportion to its locked-rotor kVA against the source's short-circuit strength. Screen it as dip ≈ 100 × S_start/S_sc at the point of common coupling, then refine with ΔV = I_start(R cosφ + X sinφ) per phase. In the worked 11 kV, 1.5 MVA chiller example a direct-on-line start gives 3.6% at the PCC and 4.0% at the plant bus, failing a 3% limit; a 65% tap autotransformer or a soft starter limited to 3× rated current holds both points under 2%.
Troubleshooting
Identifying unknown terminals on a NEMA size 1 motor starter
Those unmarked terminals are auxiliary contacts on an adder block. With the starter locked out and verified dead, confirm each pair by resistance: open with the armature released and a fraction of an ohm when pressed marks a normally open contact. Wire that pair across the Start pushbutton as the seal-in, and put the overload's normally closed contact in the coil return.