Variable frequency drives
Variable frequency drives: sizing, parameters, cabling, filters, braking and fault finding.
Latest articles
Selection guide
Sizing a VFD for a three-phase motor on single-phase input
On single-phase input, size the drive's continuous output current at no less than twice the motor nameplate full-load amps when the drive's 50% derating applies, and feed it from a branch circuit sized to 125% of the drive's published single-phase input current — never from the ideal wattage estimate. For a 10 hp, 208 V motor that means a drive rated at least 61.6 A output.
Selection guide
Choosing a line reactor or motor reactor for a VFD
Pick the side first. A line reactor goes between supply and drive input, sized on drive input amps at 3% impedance for transient buffering or 5% for harmonic reduction; a motor reactor goes between drive output and motor, sized on motor FLA, for reflected-wave protection on long shielded leads. The two are not interchangeable.