Wiring, grounding and bonding
Grounding, bonding, conductor sizing and wiring practice for industrial panels and machines.
Latest articles
Troubleshooting
Locating a ground fault on a resistance-grounded 480 V system
Phase-to-ground readings of 420, 380 and 77 V with all phase-to-phase voltages at 480 V mean the neutral has shifted toward P3: a first ground fault on P3, its current limited by the neutral grounding resistor. Locate it by resistor voltage and current, timing against process events, then feeder-by-feeder isolation, because a second fault on another phase becomes a phase-to-phase fault through ground.
How-to
Installing a robust PROFIBUS DP network inside an MCC
Run the bus at or below 1.5 Mbit/s, keep the cable against the bonded backplane, clamp the shield to bonded metalwork at every MCC entry, and terminate only the two electrical ends of the segment: a slower rate widens timing margins but cannot fix poor bonding or missing termination.
Explainer
Converting a 4-wire switchboard to 3-wire generator service
Yes — run both service switchboards 3-phase, 3-wire, with every 277 V load moved to a separately supplied panel, and bond the generator neutral to the grounding electrode system at the paralleling switchgear only, as a separately derived system under NEC 250.30. The listed 4-wire boards then need the neutral bus removed, isolated or field-evaluated, and the ground-fault sensing redesigned for a system with no neutral.
Troubleshooting
Diagnosing 200 A currents on equipment grounding conductors
Hundreds of amperes on equipment grounding conductors between a substation and its MCCs, with like phases grouped in cable tray, is magnetically induced circulating current, not a ground fault. Clamp all circuit conductors of one feeder: a residual near zero proves induction, and the fix is regrouping each parallel set A-B-C.