Motors and motor starters
Earlier articles
How-to
Wiring a three-pole contactor for a single-phase motor
Run the single-phase current through two poles in series per the overload maker's diagram — supply to terminals 1 and 5, a link between 3 and 6, motor leads at 2 and 4 — and never parallel all three poles. Set the overload at 125% of the 6 A nameplate full-load current (7.5 A) when the service factor is 1.15 or higher or the temperature rise is 40 °C or less, otherwise 115% (6.9 A), per NFPA 70 (NEC) 430.32.
Troubleshooting
Motor running over nameplate amps after soft starter bypass
The motor averages 192.7 A against 164.0 A FLA with only about 0.90% voltage-magnitude unbalance, so the supply is not the proven cause. Treat excess shaft load or excess motor loss first, and confirm negative-sequence voltage with a three-phase power-quality analyzer reading V2/V1, total kW and speed before replacing the starter or the motor.
Selection guide
Selecting overload and jam protection for a reversible motor
Set a bimetallic or electronic overload relay from the motor's nameplate full-load current — never from wattage — and give the electronic-clutch trip to a separate current-sensing jam or shock relay set above the highest normal process current. Its adjustable reset delay must outlast the cycle timer's worst-case command drop-out, and auto reset needs a deliberate-restart decision because a live run command restarts the motor.
How-to
Wiring a three-phase coolant pump starter from a 120 V signal
Run the machine's 120 V coolant output through the overload relay's normally closed contact to a contactor with a 120 VAC coil, and set the overload dial to the pump's nameplate full-load current — 1.8 A on a typical 1/2 HP three-phase pump, inside a 1.3–2.1 A adjustable range. Then bump-test rotation and swap any two motor leads if the pump runs backward.
Explainer
Motor starter vs contactor: using a starter as one
A motor starter is a contactor with an overload relay added: the relay's normally closed contact opens the coil circuit on sustained overcurrent. A starter works wherever a contactor is called for, provided three checks pass — horsepower rating at the supply voltage, coil voltage, and the overload setting against the motor's nameplate full-load current. A NEMA Size 1 covers a 3 HP motor.