Control power: 24 V DC, UPS and transformers
Control power supplies, 24 V DC distribution, UPS units and control transformers.
Latest articles
How-to
How to fuse a dual-output 115/230 V transformer secondary
The two loads total 2,415 VA, so the 2 kVA transformer is undersized: fit a 3 kVA unit and fuse the secondary leads at 125 percent of the current each actually carries — 15 A in the shared X1 lead, 10 A in X4. Bond the X2–X3 junction, never fuse the grounded lead, and apply the NFPA 70 (National Electrical Code), 2023 edition, Article 450.3(B) percentages.
Troubleshooting
Feeding a 240 V control transformer from a high-leg delta
Yes. A control transformer primary responds only to the voltage across its two terminals, and on a high-leg delta every pair of lines delivers the full line-to-line voltage, so a 240 V primary on a 120 V leg plus the high leg is correctly fed. The 60 V per secondary lead to ground is a reference artifact, and the dropout is found by measuring across the contactor coil while it tries to hold.
Troubleshooting
Sizing a step-down transformer for a 110 V UPS
Size the transformer at 1.25 times the UPS VA rating: 625 VA minimum for a 500 VA UPS, so 750 VA is the practical choice. If breaker trips survive a transformer and UPS swap, the cause is the wiring between the two-wire 110 V secondary and the three-pin UPS plug, not the VA rating.
How-to
Powering a 208 V VFD from single phase to program it
Land 240 V single phase on any two input terminals of a 208 V-class three-phase drive and leave the third open: the diode bridge charges the DC bus to roughly 340 VDC, so the keypad, control supply and parameter memory run normally. Never enable the output on this bench feed.
Troubleshooting
Why a control transformer secondary shows voltage to ground
The 42 V that climbs to 76 V as loads start and jumps to 131 V on the start button is capacitive coupling through a floating control transformer secondary, read by a 10 MΩ meter — not coil current. Meter across the coil and across X2-XF: about 0 V across the coil stopped and a steady nominal voltage across X2-XF means the circuit is healthy. Then the schematic decides whether X2's designed bond is open or the secondary runs floating.
Explainer
Grounded or floating control power transformer secondaries in MCCs
Ground the secondary, on the return terminal that the bucket breakers do not switch. A floating 230 V winding with no insulation monitor gives you a first earth fault no breaker clears and leaves bucket wiring live after its breaker opens; floating only earns its keep with an insulation-monitoring device and double-pole breakers, neither of which this MCC has.
Selection guide
Measuring DC and AC motor current for a PLC without a VFD
No. A fixed-speed motor that keeps its starter and overload relay gets PLC current feedback from a current transducer wired to an analog input, or from a communicating overload relay that reports over the network. A 12 V DC load needs a DC-capable Hall-effect transducer, because a current transformer cannot read steady DC.
How-to
Using 208Y/120 phase-to-neutral control power without a transformer
Yes. A 208Y/120 source delivers 120.1 V phase to neutral (208 V ÷ √3), inside the input window of most 115 VAC control components, so the control transformer can be deleted when an insulated neutral physically reaches the panel, the loaded voltage sits inside every component's datasheet range, and branch protection carries an interrupting rating for the mains available fault current. If the neutral cannot be pulled or the fault level outruns the protection, keep the transformer, outside the panel if space is the only issue.